Viessmann F2 Fault Code: Temperature Limiter Tripped

Quick answer

F2 on a Viessmann Vitodens boiler means the temperature limiter has tripped, so the boiler overheated and shut down. Viessmann's first checks are the system fill level, the pump and air in the system. Check the pressure and top up to around 1 to 1.5 bar if it is low, but if F2 returns after a reset you need a Gas Safe registered engineer.

On this page
  1. What the F2 code means
  2. Common causes of F2
  3. Safe checks you can do yourself
  4. When to call a Gas Safe engineer
  5. Typical repair costs in the UK
  6. How to stop F2 coming back

What the F2 code means

On the Vitodens 050-W and 100-W, Viessmann's service instructions describe F2 as "temperature limiter has responded". The temperature limiter, sometimes called the high limit thermostat, is a safety device that cuts the burner if the water in the boiler gets far hotter than it should. It works separately from the normal temperature control, so when it trips, something has stopped heat being carried away from the boiler.

The boiler puts the burner into a fault state and shows F2 until it is reset. On the Vitodens 100-W the fault symbol usually flashes with the letter R to show a lockout. Older Vitodens generations use F2 for the same kind of fault, but always check your own manual.

Because the limiter is a last line of defence, we treat F2 as an engineer fault. There are a few simple checks you can make first, but a boiler that overheats more than once needs proper investigation.

Common causes of F2

Viessmann's service instructions list the heating system fill level, the circulation pump, venting the system and the limiter and its connecting leads. These are the usual causes behind those checks.

Low water pressure

If there is not enough water in the system, circulation suffers and the heat exchanger overheats. This is the first thing to look at.

Air in the system

Air trapped in radiators, pipework or the pump stops water moving freely, so heat builds up inside the boiler.

Pump problems

A pump that is stuck, slow or failed cannot move enough water. Pumps often stick after a quiet summer.

Restricted flow

Sludge in older systems, a blocked filter or most radiator valves being closed can all reduce flow through the boiler.

Faulty limiter or wiring

Less often, the limiter itself or its connecting leads are at fault, so it trips when the boiler is not actually overheating.

A quick way to tell them apart

If F2 appeared soon after you bled radiators, drained the system or noticed the pressure dropping, low water or air is the likely culprit. If the pressure is steady and the radiators are hot all over, but the boiler still trips, the pump, a restriction or the limiter itself becomes more likely, and that needs an engineer.

CauseTypical signWho fixes it
Low pressureGauge below 1 bar when coldYou, via the filling loop
Air in radiatorsRadiators cold at the top, gurglingYou, by bleeding radiators
Air in the pump or boilerNoisy boiler after draining or refillingGas Safe engineer
Pump faultHumming, radiators stay coolGas Safe engineer
Sludge or blocked filterCold patches at the bottom of radiatorsGas Safe engineer
Faulty limiter or leadsF2 with good pressure and circulationGas Safe engineer

Safe checks you can do yourself

  1. Let the boiler cool down before you do anything else.
  2. Check the pressure gauge or display with the system cold. If it is below 1 bar, top up with the filling loop until it reaches around 1 to 1.5 bar, or the figure in your manual, then close the valves fully. Our guide on how to repressurise a boiler explains each step.
  3. If any radiators are cold at the top, bleed them with the heating off, then check the pressure again.
  4. Check your thermostat, timer and radiator thermostatic valves so that several radiators are open.
  5. Reset the boiler as your manual describes. On the Vitodens 100-W, press and hold R for about two seconds. Stop after two or three attempts.

Do not remove the casing to vent the pump or test the limiter. These parts sit next to the burner and gas valve and must only be handled by a Gas Safe registered engineer. If you hear loud banging or smell burning, switch the boiler off at the fused spur and get it checked.

When to call a Gas Safe engineer

Call a Gas Safe registered engineer if F2 comes back after the pressure has been corrected and the radiators bled, or if the boiler has overheated more than once. You should also call if the pressure keeps dropping, as that points to a leak or a problem with the expansion vessel.

The engineer will check the pump, vent the boiler properly, test the temperature limiter and its leads, and look for restrictions such as sludge or a blocked filter. Tell them the pressure reading, whether you have topped up or bled radiators, and any noises you have heard.

Typical repair costs in the UK

If topping up and bleeding clear the fault for good, there is no cost. Otherwise, these ranges are typical. Your final bill depends on the model, parts and area.

JobTypical UK cost
Engineer call-out and diagnosisTypically £80 to £150
Temperature limiter replacementTypically £100 to £200
Pump replacementTypically £250 to £450 fitted
Magnetic filter fittedTypically £150 to £250
System clean or powerflushTypically £400 to £700

How to stop F2 coming back

Check the pressure monthly and keep it in the normal range when cold. Run the heating briefly now and then over the summer so the pump does not stick. If you keep losing pressure, see our guide on a boiler leaking water, and if it climbs too high when hot, our guide on boiler pressure that is too high explains why. A yearly service lets an engineer check the pump and system water quality, and our boiler service cost guide covers what is included.

Frequently asked questions

What does F2 mean on a Viessmann boiler?

It means the temperature limiter has tripped because the boiler overheated. The burner stops until the boiler is reset.

Can low pressure cause Viessmann F2?

Yes. Viessmann lists the system fill level as the first check. Low pressure and air reduce circulation, which lets the boiler overheat.

Can I fix Viessmann F2 myself?

You can top up the pressure, bleed radiators and reset the boiler two or three times. If F2 returns, the pump, limiter or system needs a Gas Safe registered engineer.

Is Viessmann F2 dangerous?

The limiter tripping is a safety feature, so the boiler is protecting itself. Repeated overheating should not be ignored, and it needs an engineer to find the cause.

Other Viessmann fault codes

Full list →

Fault code meanings can differ between boiler models and software versions. Always check the user manual for your exact model. This page is general information, not a substitute for an inspection by a Gas Safe registered engineer. Read our disclaimer.